1

Devices I am using are:

1) Songle 2 channel relay module - https://www.electronicscomp.com/2-channel-5v-relay-module-with-optocoupler?gclid=CjwKCAjwvuzkBRAhEiwA9E3FUnbadf71q6h2pX_VsmrUK6x0c9dHQm9aZ0EjEIRIoKsbmvFoRhY96xoCbcUQAvD_BwE

2) Breadboard power supply module - https://robu.in/product/mb102-breadboard-power-supply-module-3-3v5v-arduino-solderless-bread-board/?gclid=CjwKCAjwvuzkBRAhEiwA9E3FUv8xyHVyNeRe8mcrdalrsXgTt5vg0q4JGdTITGhJbK6W5PAdKWy4XRoC64YQAvD_BwE

Connections which I have done are :-

Do keep in mind that I have used the Raspberry Pi for only GPIO pins connection to IN1 and IN2 of the relay module and power supply to the relay module is from that breadboard power supply module I have put the link to above.

1) JD-VCC of the relay module to 5V of the power supply module.

2) VCC of the relay module to 3.3V of the power supply module.

3) GND of the relay module to the ground of the power supply module.

4) IN1 and IN2 of the relay module to Raspberry Pi's GPIO 13 and GPIO 6 pins. (No power supply is there from the Raspberry Pi).

only the relay status led is getting blinking, but not the relay switching sound is not being heard.

tlfong01
  • 4,847
  • 3
  • 12
  • 24
Aditya Raghu
  • 39
  • 1
  • 5

2 Answers2

2

The specification of the relay board you linked to says it requires 12V to operate it.

Bra1n
  • 1,261
  • 7
  • 8
2

Solution 1 - Add a resistor at the input terminal

Short Answer

Add a 4k7 resistor at the IN terminal. Rpi should now switch on/off the relay without any problem. Yes, it is that simple. If 4k7 does not work, read the long answer below to find a value that works.

Add 4k7 to IN

Long Answer

The OP's relay is optoisolated, low level triggered designed for 5V Arduino. This type of relay switches on if input signal is less than 1V, and switches off when input is greater than 4V.

Arduino has no problem because its high low signal meets the spec. However, 3V3 Rpi's low signal meets spec, but high signal is only around 3V, therefore cannot switch off the relay. In other words the relay is always on.

There are 5 methods to get around, and a schematic is helpful to explain.

Low trigger relay circuit analysis

Now a picture of the real thing - the OP's relay and two similar relays I am testing.

OP's relay and two similar ones

Now I am using a jumper wire to connect IN to the following voltage levels, (1) Ground, (2) 5V, (3) 3V3.

Green LED is on if IN = 0V (Gnd), off if IN = 5V. In other words, it 5V logic compatible.

Howeve, Green LED is still on if IN = 3V3. This means 3V3 is not high enough to switch off.

I checked that the IN current at 0V = 3.8mA, at 5V = 0.001mA, but at 3V3, current is still high, 0.6mA.

in signal = 0V, 5V, and 3V3

Now that for the fixed input values of oV, 3V3, and 5V, the currents are 3.8mA, 0.6mA, and 0.002mA, and corresponding status of relay are On, On, Off. To make the relay 3V3 logic or Rpi compatible, the 3V3 current should be so small to cut off the optocoupler and therefore relay off.

To look at the whole picture of the relay characteristics, I used a adjustable voltage power supply to check the If vs In voltage, and plot a graph as below. Now I can see the trigger point is < 3.62V (On) and > 3.84V (off).

I need to modify the circuit so that the trigger band shifts down to below 3V, Rpi's High signal value.

Relay optocoupler infrared LED current vs In signal

Actually it is very easy to shift the trigger band down to below 3V. The trick is to note that the corresponding trigger current is around 0.15mA (highlighted in orange). So just increase the current limiting resistor so that the current is below 0.15mA when Vin ~=3V (or 2.8V, to add a little bit of safety margin).

But if modified current limiting resistor too large, then photo transistor won't saturate. So I did a couple of trials and errors and found 4k7 seems a good choice. The engineering trade off / experimentation is selfied below.

Solution 1 - add 4k7 to IN terminal

Now I have checked the LED current vs Vin from 0V to 5V, to make sure that the trigger band is not too narrow to cause a stability problem. So far so good.

Next step is to use a python program to verify that Rpi GPIO ~3V/~0.5V High/Low signal can directly drive the modified 5V relay.

Modified (adding 4k7 to IN terminal) If vs Vin graph .
.
.
.
.

/ to continue, ...

The very long answer below is to be shortened later

I am 90% sure that your module cannot be directly controlled by Rpi. I will first point out the problems, then suggest ways to get around.

enter image description here

I will search my junk box to find a relay similar, and do some experiments to verify my guesses are correct.

Luckily I found a similarly looking guy. First thing first is to check out if it is (1) low logic level activate/triggerable, and (2)5V Logic compatible.

Me no English, so I selfie!

To show module (1) low activate, (2) 5V logic

Now that I know the relay module switches on when In1 is Ground, and off when In1 is 5V, I move on to test (a) how high, say, 3V or 4V can still turn it off, and (b) how low, say, if 1V or 2V can still turn it off.

There you go, selfies again.

Finding relay activate/deactivate signal voltages

Earlier I though my module similar to the OP is not Rpi compatible either. But I surprising found that its trigger points are approximately 1.8V- and 2.4V+. Since Rpi's low level is < 1V, and high level > 2.8V, therefore Rpi has no problem switching it on/off. (Arduino high/low are approximately < 1V and > 4V, so also has no problem.)

So now I still need an example similar to the one OP has, to explain why Rpi's low signal is OK to switch it on, but Rpi's high signal is not high enough to to switch it off (without fiddling with the JD-Vcc jumper, which most newbies never heard of!). I searched my junk box again, and did similar engineering experimentation with the results below.

enter image description here

Now the time has come for me to answer the OP's question about using the JD-Vcc way of supplying power to the relay, and an example of Rpi Python code to control it.

I am using a relay recommended by Forbes. You might like to read the following Forbes article before I explain. But the picture first.

Everything You Need To Set Up Raspberry Pi Home Automation - Don Reisinger, Forbes (recommending an optoisolated, low level trigger relay) https://www.forbes.com/sites/forbes-finds/2018/07/12/everything-you-need-to-set-up-raspberry-pi-home-automation/#7c65bdb04cdb

Forbes low trig opto relay

Will this code harm rpi, and how does JD-Vcc work?

GPIO.setmode(GPIO.BCM) ... code used to trigger relay using raspberry pi, connected 5v source to jd-vcc and 3.3v to vcc of header. Is there any harm in using the above ...

connected 3.3V of relay to 3.3V of the RPi. JD-VCC to 5V of the power supply. ground of relay to ground of power supply. Now it's working. The question now is, why isn't the relay working when I connect the VCC of the relay to 3.3V of the power supply. ...

To answer the above questions, we need first to see how the photocoupler works. Here is the picture.

EL87C and EL354 Photocoupler summary notes

Now that we know the specification of the photocoupler, we can do some quick and dirty calculations, to make sure that the relay will not harm you rpi GPIO.

Not using Rpi's 40 pin connector's 5V, 3V3 power pins to power relay

Just now I read your question again and I gave it an up vote, because of the more than ten user questions I read so far about this FAQ topic, yours has the most detailed description of the frequent newbie problem of Rpi not being able to turn off a low level trigger relay which Arduino has no problem, because the relay was designed for Ardunio, perhaps before Rpi was born.

I particularly appreciate your specifically pointing out that you are using the external power supply unit, even with a web link. This is a very important guideline for newbies often connecting the wrong wires by mistake. Actually I have been using Rpi for 5 years, and I NEVER USED the RPI's 40pin connector power pins to power any external device.

Low Trig Opto EL817C 5V Relay Rpi GPIO Input Current Requirement Calculation

enter image description here

Working backwards, Ic needs only 1mA. Working forward, If 5mA would generate 10mA Ic, fully saturate photo transistor. Conclusion - Rpi GPIO Low need only 5mA to fully saturated photo transistor.

The question is Rpi GPIO High too High to cut off photo transistor?

Now I am going to measure the current flowing into low level signal (power ground, or Rpi low). The objective is to check if current flowing into Rpi GPIO signal pin is too large to damage the Rpi. I am going to check two types of low level relays, (1) without optoisolation, (2) with optoisolation, similar to the OP's relay. The results shows that for this relay, signal current is between 0mA~4mA, safe enough for Rpi, but not compatible to Rpi, because Rpi High is not high enough to switch on this relay.

The second relay tested is low trigger PNP type relay, as shown on the left of the schematic below. One way to get around the Rpi high level signal is not high enough problem is to increase the series resistance, so that less current flows into the LED and therefore cannot drive the photo transistor into saturation.

Next to measure the current for OP's opto isolation type low trigger relay.

No opto isolation relay low signal current measurement

Now I am measuring the currents of the optoisolated, low level trigger relay that looks similar to the OP's dual relay module. However, the OP's module does not work with Rpi, unless Vcc = 3V3, and JDVcc = 5V. For this relay just tested, JdVcc = Vcc = 5V works for both Arduino and Rpi.

enter image description here

If If is only -2mA, I need to check the CTR at this point and see if Ic and Vce(sat) etc. So I checked out the CTR pic and found CTR at 2mA is 70%. So Ic is 2mA * 70% = 1.4mA, should be safe enough, ...

EL817C CTR at If = 5mA

To avoid frying Rpi, first test manually, by hand, using a jumper wire to select hardware signals, from breadboard PSU module, 5V, 0V, 3v3 power rail, and 555 square wave etc, to test relay, BEFORE using Rpi GPIO by python program.

Youtube showing a NE555 timer 1Hz square wave, switching on/off a 5V Rpi incompatible, low level trigger, optoisolated Relay

Summary of three Relays Tested So Far

Now I am going to write a Rpi Python program to toggle the third relay module. First, a summary of the three relay modules so far tested.

(1) 5V dual channel, with optocoupler, low level trigger. This relay is identical to the OP's relay, except one thing:- OP's relay is NOT Rpi compatible. This one is. Because I cannot repeat OP's failures using this module, so I found the second relay to try.

(2) This relay module has not optocoupler, but only one PNP BJT directly driving the Songle relay switch. Since this is not like OP's module with optoisolation. So I tried another one.

(3) This is similar to OP's modules, but only single channel, and without JDVcc jumper for separate control logic and relay switch power supplies. I found this NOT Rpi compatible, so is ideal to test out for the OP's question.

The Rpi Python Program to use logical level shifted up GPIO signal to drive relay.

OP has at least three ways to get around, (1) Using JDVcc and Vcc PSU, (2) Setting GPIO pin to input, in order to switch off the relay, (3) using a logical level shifter to convert Rpi GPIO 3V level to 5V.

I think the first two solutions are not safe for newbies. For newbies, I recommend to shift Rpi 3V signal to 5V. The program written below is for this solution.

Now I have debugged a little python program to toggle the relay which in turn drives a 12VDC motor and a 12VDC solenoid at the same time.

Next step is to check the level of back EMF, EMI which transmit back to the Rpi side and successfully isolated by the optocoupler, ...

youtube of Rpi driving relay to control 12VDC motor and solenoid

Back EMF Check of Four Inductive Loads (Motor, Solenoid, Water Pump, Solenoid Valve)

enter image description here

enter image description here

youtube video of relay driving 4 inductive loads

Optoisolated Back EMF Voltage

Input signal seems almost completely optoisolated. Next is to compare relay WITHOUT optoisolater.

enter image description here

enter image description here / to continue, ...

tlfong01
  • 4,847
  • 3
  • 12
  • 24